Automation, Control, Data Acquisition, and Remote Applications

Started by vietthum at 05-22-2007 8:54 AM. Topic has 4 replies.

Print Search
Sort Posts:    
   05-22-2007, 8:54 AM
vietthum is not online. Last active: 4/5/2007 11:19:42 PM vietthum

Top 150 Posts
Joined on 04-05-2007
Posts 2
How to get the totalizer value from analog input
Hello,

I am the newcommer with OPTO22.
I use SNAP-PAC-R1.

1. I want to get the totalizer value from analog input (flowrates) from a flow meter. How to do it?

2. I want to get the totalizer value from Digital input from Pulse of flow meter. And I want to calculate the flowrates from this Pulse input. How to do it?

Could any one help me please?
Above 02 question can be solved in SNAP-PAC-R1?

Thanks & Best regards,
Nguyen Vinh Loc


   Report 
   06-15-2007, 1:36 PM
Fuji is not online. Last active: 6/16/2007 4:23:52 AM Fuji

Top 500 Posts
Joined on 06-16-2007
Posts 1
Re: How to get the totalizer value from analog input
I found that the easiest way to totalize water flow was to use pulse counting.. as you have listed as your second point. If your flow meter has an open collector output - make sure the supplied voltage is within the range of your digital input card. Other than that, you just need to write a simple strategy to apply your multiplication factor.


And yes.. the R1 can perform high speed counting.
   Report 
   06-26-2007, 9:46 AM
Barrett is not online. Last active: 11/12/2005 8:06:39 PM Barrett

Top 10 Posts
Joined on 04-07-2004
St. Louis, MO
Posts 27
Re: How to get the totalizer value from analog input
If you still need help on this, let me know.
You have to keep in mind that the accuracy of you input is relative to how long a period you count before clearing and restating the count in the module before you pull the count in for the math conversion. The amount of counts versus the fraction of pulse you actually do not recieve in the process of retriving the count. You can also use pulse for rate but this is sensitve to the pulse rate and if you do this, you should condsider using two input points on a "Fast" module and use one for counting and the other for pulse period or freq to get the rate input. barrett@automateco.com
   Report 
   06-26-2007, 4:48 PM
Kiwi is not online. Last active: 4/12/2007 9:11:11 AM Kiwi

Top 75 Posts
Joined on 04-12-2007
Posts 4
Re: How to get the totalizer value from analog input

Hi,

   A simple way of intergrating an analog input is to Set up a timed instruction to add the input value every few seconds to a variable. e.g. if you have a flowmeter FT-XXX range 0-100 L/m and supposing the flow is at 45 L/m and your instruction executes every 6 seconds.

Divide FT-XXX by 10 (60/6=10 times per minute) and your instruction adds 4.5 to the variable every 6 seconds (4.5 x 10 = 45)

Of course you don't have to use 6 seconds you would get the same results by 45 / 20 every 3 seconds.

It's also easy to change your units for example Liters to M3     FT-XXX/10,000 every 6 seconds would give you 0.045

The main thing is to make sure your timer is accurate, use the real-time clock  with a "GetSeconds" instruction rather than just a timer or wait instruction

It can be a little tricky but its easy to test by using a dummy variable in place of the flowmeter.

If your flow is very eratic, you may need to include a filter to smooth it out.

Hope this helps

Roy 


   Report 
   09-04-2008, 7:50 AM
nvl is not online. Last active: 7/12/2007 10:59:52 PM nvl

Top 10 Posts
Joined on 07-12-2007
Posts 17
Re: How to get the totalizer value from analog input

I make a flow chart with an up timer with 1 second. The totalizer is accurate in short time, just few minutes.

But the error will be bigger in long time. I found that:

There is a small time delay since the controller knows the up-timer is expired to the time it starts the up-timer again.
==> the actual total time for totalizing is = up-timer value + small time delay.
==> it causes the error.

and the problem is we can not count this small time delay. It varies, from 3 to 5ms. if it is constant, we would compensate for error.

==> do you know how to fix this small time delay?

In other words, do you have any other technique for totalizing a float value (not only analog input)? It must be accurate technique.


   Report 
OptoForums » Application For... » Automation, Con... » How to get the totalizer value from analog input