$399.00 (USA and Canada only)
Input
12-bit serial data (each channel)
Outputs
0 to 20 mA (each channel)
Span
20 mA
Resolution
4.9 microamps
Response Time (% of span/delta I/ delta time)
99.9%/15.98 mA/3 mS
DC Common Mode Rejection
>-120 dB
AC Common Mode Rejection
>-120 dB @ 60 Hz
250 V
Common Mode Resistance
>1000 Megohms
Accuracy
0.1% of Span
Gain Temperature Coefficient
50 PPM/°C
Offset Temperature Coefficient
20 PPM/°C
Module Power Requirements
5 Volts DC (±0.15 ) @ 150 mA
Loop Power Requirements
8 Volts DC (min) to 32 Volts DC (max)
Max. Loop Resistance (Ohms) @ Loop Supply
250 8V
450 8V
650 12V
1050 24V
1450 32V
Max. Loop Resistance formula
(Loop Voltage - 5) 0.02
Ambient Temperature: Operating Storage
-20 °C to 70 °C -40 °C to 85 °C
Humidity
5-95%, non-condensing
Torque, hold-down screws
Torque, connector screws
5.22 in-lb (0.59 N-m)
Wire size range
22 to 14 AWG
UL, CE, ATEX, RoHS, DFARS; UKCA
Lifetime
This document lists and describes all current Opto 22 SNAP PAC System part numbers, including PAC Project software, SNAP PAC controllers, and SNAP I/O modules of all kinds. SNAP PAC mounting racks and SNAP power supplies are also listed.
SNAP I/O analog output modules are part of Opto 22's SNAP PAC System. This document includes descriptions, specifications, and wiring and dimensional diagrams for all SNAP analog output modules:
This document lists all Opto 22 part numbers that have the Underwriters Laboratory (UL) approval.
$104.00