How a nationwide bank restored critical cooling without infrastructure changes
A nationwide bank's headquarters in Australia supports critical IT infrastructure for banking operations across the continent. Keeping this data center equipment at a functioning temperature contributed to the bank’s rising energy costs.
In 2022, a building-wide HVAC refit removed a central chiller to improve the facility’s energy efficiency. In its place, individual cooling systems were installed on each floor to regulate temperature independently.
But what no one realized at the time was that the original chiller also cooled the bank’s backup generator.
Routine testing gave the bank confidence that its backup generator was storm-ready—until late 2023, when a major storm hit. Power failures forced the generator to run for extended periods, but without the chilled water from the old system, it overheated and shut down, putting the entire banking network at risk.
Critical Cooling—But No Infrastructure Modifications
Fixing the cooling issue wasn’t as simple as installing a new system with new sensors and controls.
Strict building regulations prohibited drilling into walls, floors, or ceilings, meaning no new conduit runs between floors. The solution had to work with the building as it was, using only existing cable pathways.
To restore cooling, the bank installed a radiator on the building’s roof and repurposed existing copper piping to circulate coolant. A three-phase fan pulled air across the radiator, dissipating heat before the coolant returned to the generator, creating a closed-loop cooling system.
But the bank wanted better monitoring and control than ever before. Restoring cooling wasn’t enough—the new system had to provide real-time diagnostics, alerts, and automation to make sure the problem never happened again.
The rooftop radiator of the bank's headquarters
Bringing the Right Partners Together
For over 20 years, ProSwitched™ has provided electrical and process control expertise for the nationwide bank. When the bank’s on-site electricians needed a smarter monitoring and automation solution to keep their generator online, they relied on their long-time partner for support.
To enhance industrial automation and IIoT capabilities, ProSwitched turned to Binford Tech™, an Australian industrial controls distributor, to supply the necessary hardware and technical expertise.
To keep the generator online, they needed to develop an automated solution that integrated seamlessly with existing infrastructure—requiring no structural modifications and using existing cable pathways.
Smart Sensors Need Smart Control
Early on, Binford Tech and ProSwitched identified IO-Link® as a way to simplify installation and enhance diagnostics without adding new wiring. They selected SICK® IO-Link sensors to provide real-time monitoring of key parameters:
  • FTS-I100F14B thermal flow/temperature sensors to monitor coolant flow and temperature.
  • PBS2-RB010SG1SSDNMA0Z pressure sensors to track system pressure and detect anomalies.
These sensors digitally transmit their data over a single cable, making installation easier within the existing infrastructure. To manage the IO-Link devices, the IFM® AL1122 and AL1120 IO-Link masters were deployed, enabling seamless Ethernet/IP communication to the control system.
But sensors and IO-Link masters weren’t enough—the system needed a controller that could integrate everything over Ethernet, providing real-time data processing and automation to keep the generator running reliably.
That’s where the Opto 22 groov EPIC® came in. More than just a PLC, the groov EPIC (Edge Programmable Industrial Controller) combines real-time control with built-in networking, data processing, and secure access. It also includes groov View® for built-in, web-based, and local visualization that allows operators to monitor and adjust the system from any connected device.
To further enhance monitoring, a groov RIO® Energy Monitoring Unit (EMU) was installed to track voltage, current, and power conditions, ensuring stable operation and helping detect fluctuations that could impact generator performance.
With direct Ethernet integration to groov EPIC, the groov RIO EMU provided real-time energy data with simple software configuration and no complex wiring.
groov EPIC handles central control from the generator room.
groov RIO EMU tracks power conditions to ensure stable generator operation.
CODESYS Control Engine
For the bank’s application, Binford Tech and ProSwitched used CODESYS®, a PLC programming environment and runtime that allows for flexible IEC 61131-3-compliant programming. Each groov EPIC includes a free CODESYS runtime license, enabling advanced communications and control logic without any added cost. The team used several CODESYS capabilities:
  • IEC61131-3 program logic—monitoring and controlling equipment in real time
  • Modbus®/TCP communication to Variable Speed Drives (VSDs)—controlling cooling system pumps and fan speeds
  • Ethernet/IP communication to IO-Link master devices—integrating with smart sensors for real-time monitoring
  • OPC UA® server for communication to groov View—allowing visualization for operators to monitor system performance and adjust setpoints
“groov EPIC’s ability to talk to so many devices at once made this project possible. It gave us better control, better monitoring, and way more insight than we’ve ever had before,” says Justin Anderson, Industrial Electrician with ProSwitched.
The nationwide bank uses the CODESYS development platform for real-time control.
groov View for Visuals and Alerts
Every groov EPIC includes a web-based visualization platform called groov View, which runs both on the groov EPIC’s LCD display and on any network-connected devices. The bank’s application used groov View for the following features:
  • Monitoring—to display real-time data from temperature, pressure, and flow sensors
  • Adjustments—to let operators modify setpoints and control parameters remotely
  • Alerts—to send email notifications when generator cooling thresholds are exceeded
  • Troubleshooting—to provide historical trends and diagnostic data to identify potential issues
“groov View gave us exactly what we needed—local monitoring, on-site control, and automated alerts—all without adding extra HMI or display hardware,” says Anderson.
Results: A Storm-Proof Solution
At the end of 2024, the bank’s backup generator faced its ultimate test—an entire storm season with multiple outages—and passed without a single failure or shutdown. What was once a critical vulnerability is now a self-regulating system that keeps power stable no matter the conditions.
Real-time monitoring ensures that if a pump slows or a fan underperforms, the system responds instantly—no manual intervention required.
What was once a last-minute scramble during power failures is now a fully automated, hands-off system. No drilling, no costly infrastructure changes—just a smarter, more resilient solution that keeps the critical servers running when it matters most.
Rooftop views: new radiator pipes connected to existing copper pipes
Future Prospects
With a full storm season behind them and zero failures, the bank and its partners are now looking to enhance the system further.
The next step is remote monitoring via the secure OpenVPN® client included on all groov EPIC processors, allowing operators to check performance and troubleshoot issues without needing to be on site.
They are also exploring direct generator integration, using groov EPIC’s myriad communication options to pull real-time data on fuel levels, runtime, and system health to provide deeper insights and faster response times if issues arise.
With Binford Tech and ProSwitched’s modular approach and groov EPIC’s flexibility, the bank can continue scaling without major infrastructure changes, making future upgrades seamless and cost-effective.
Reflecting on the transformation, Anderson sums it up: “Before this, we had no diagnostics, no feedback—just hoping things worked. Now, with real-time monitoring and automation, we know the generator will stay online when it matters most. It’s not just a fix, it’s a future-proof solution.”
About ProSwitched
Headquartered in Bundaberg, Australia, ProSwitched outdoes their competition because of the well-trained and experienced electrician at the helm. They have a vast range of experience in the domestic, commercial, and industrial sectors. They offer their clients exceptional services using the highest quality products. Expert knowledge of electrical installations and maintenance strategies allow them to deliver the best possible solutions to meet all requirements.
About Binford Tech
Headquartered in Australia, solution-based company Binford Tech excels in turning the intricate challenges faced by the fast-moving consumer goods (FMCGs), OEMs, and Process Automation sectors into opportunities for innovation and growth. With over two decades of IoT and Smart Manufacturing expertise, they lead the charge towards more efficient, sustainable industry practices. They are committed to solving complex problems and empowering clients with tailored, cutting-edge solutions.
Featured Product:
groov EPIC & groov RIO
groov EPIC groov RIO
Order now!