SNAP-AITM-4i
SNAP-AITM-4i
$630.00 (USA and Canada only)
SNAP 4-Ch Isolated Type B, C, D, E, G, J, K, N, R, S, or T Thermocouple or or +/-150, +/-75, +/-50, or +/-25 mV Analog Input Module
The versatile SNAP-AITM-4i module provides four channels of analog input with an input range of ±150 mV, ±75 mV, ±50 mV, ±25 mV, or Type B, C, D, E, G, J, K, N, R, S, or T thermocouple, and each channel can be individually configured.
The module provides optical isolation, transformer isolation, and channel-to-channel isolation. Since the four channels on the module do not share any common connections, grounded sensors and field devices may be used with them.
SNAP-AITM-4i requires SNAP PAC racks, a SNAP PAC brain or R-series controller with firmware 9.1 or newer, and PAC Project 9.1 or newer.
For a similar module with just 2 channels, see the SNAP-AITM-i.
If you don't need channel-to-channel isolation, see the SNAP-AITM or the 8-channel SNAP-AITM-8.
Input Range
From -150 mV to +150 mVDC
From -75 mV to +75 mVDC
From -50 mV to +50 mVDC
From -25 mV to +25 mVDC
Maximum Over Range
± 10%
(= ± 27500 counts)
Resolution
6 µV from -150 mV to +150 mV
3 µV from -75 mV to +75 mV
2 µV from -50 mV to +50 mV
1 µV from -25 mV to +25 mV
Cold Junction Temperature Compensation
Automatic when used with SNAP PAC brains
Input Filtering
-3 dB @ 5 Hz
Data Freshness
mV input: 75 ms
Thermocouple input: 140 ms
DC Common Mode Rejection
>-120 dB
AC Common Mode Rejection
>-120 dB @ 60 Hz
Maximum Survivable Input
±15 volts
Maximum Operating
Common Mode Voltage
250 V
Accuracy
0.06% (90 µV) @ 150 mV (full scale)
0.1% (75 µV) @ 75 mV (full scale)
0.1% (50 µV) @ 50 mV (full scale)
0.2% (50 µV) @ 25 mV (full scale)
Drift: Gain Temperature
Coefficient
5 µV / °C
Drift: Offset Temperature Coefficient
2 µV / °C
Thermocouple Accuracy [°C]
B,R,S
C,D,G
E,J,K
N,T
 From factory
±5.0
±4.0
± 2.0
±3.0
 After user gain and offset commands
±3.0
±2.0
± 0.8
±2.0
Isolation: Transformer
1500 V
Isolation: Channel to Channel
250 V continuous
(1500 V transient)
Power Requirements
5 VDC (±0.15 ) @ 150 mA
Input Resistance
100 megohms (each channel)
Ambient Temperature:
  Storage
-20 °C to 70 °C
-40 °C to 85 °C
Humidity
5-95%, non-condensing
Torque, hold-down screws
Torque, connector screws
3 in-lb (0.34 N-m)
CE, RoHS, DFARS; UKCA
Lifetime
SNAP Isolated Analog Input Modules Data Sheet
The isolated analog input modules described in this document are part of Opto 22's SNAP PAC System. They provide optical isolation, transformer isolation, and channel-to-channel isolation. This data sheet covers the following part numbers:
New Isolated Input Module for Thermocouple Temperature Monitoring and Millivolt Measurements
Opto 22’s SNAP-AITM-4i Thermocouple Input Module Provides Channel-to-Channel Isolation for Trouble-free Installation and Accurate Temperature Measurements
I/O Solutions for Temperature Monitoring (Chinese)
This white paper describes various temperature sensors such as RTDs, thermocouples, ICTDs, thermistors, and infrared sensors, and the Opto 22 solutions for using them.
Primer: I/O Solutions for Temperature Monitoring
This primer describes various temperature sensors such as RTDs, thermocouples, ICTDs, thermistors, and infrared sensors, and the Opto 22 solutions for using them.
Video: Securing SNAP Module
Video: Removing a SNAP Module
Video: I/O Solutions for Temperature Monitoring
A quick overview on I/O Solutions for temperature monitoring.
Accuracy vs Resolution