SNAP-IDC-32DN
SNAP-IDC-32DN
$278.00 (USA and Canada only)
SNAP 32-channel Digital (Discrete) Input Module, -2.5 to -12 VDC, with positive common connection
The SNAP-IDC-32DN 32-channel digital input module provides 32 digital input channels in one compact SNAP module. The SNAP-IDC-32DN is ideal for OEMs and others who have applications with high point counts, or for those requiring large numbers of digital input channels on one SNAP I/O rack. The high-density configuration reduces per-point costs of digital I/O systems by providing up to eight times as many I/O channels in the same space.
The SNAP-IDC-32DN has an input range of -2.5 to -12 VDC, and its common connections are positive rather than negative, making it ideal for NPN or sinking type inputs.
For easy field wiring, use the SNAP-IDC-HDB or compact SNAP-UDC-HDB breakout rack and the SNAP-HD-BF6 header cable. A wiring harness with flying leads (SNAP-HD-CBF6) is also available.
For sensing signals with higher current, see the SNAP-UDC-HDB-G4 breakout board, which mounts G4 input modules that handle up to 3 amps per point (G4 modules are sold separately).
If you need a similar module with a higher input range, see the SNAP-IDC-32N.
If you need a module with negative common connections, see the SNAP-IDC-32D.
Reference Charts: Build your system in the SNAP I/O Configurator.
SNAP-IDC-32
SNAP-IDC-32FM*
SNAP-IDC-32N
SNAP-IDC-32D
SNAP-IDC-32DN
Input Range
10 to 32 VDC
-10 to -32 VDC
2.5 to 12 VDC
-2.5 to -12 VDC
Nominal Voltage Range
24 VDC
-12 to -24 VDC
2.5 VDC
-2.5 VDC
Input Resistance
20 K ohms
20 K ohms
3 K ohms
3 K ohms
Logic Voltage and Current
5 VDC ± 0.1 @ 150 mA
Maximum Operating
Common Mode Voltage
250 V
250 V
250 V
250 V
Isolation: Field to Logic
1500 V
1500 V
1500 V
1500 V
Input Arrangement
32 input channels; 4 groups of 8 inputs each
Common connection
Points in each group share a common
negative connection.
positive connection.
Channel-to-Channel Isola­tion
No channel-to-channel isolation;
100 V group-to-group isolation
Hold-down screws
Connector screws
Torque: Not to exceed 1 in-lb (0.11 N-m)
Torque: 5.22 in-lb (0.59 N-m)
Maximum Number of HDD Modules on One Mounting Rack
16
16
16
16
Indicators
None; use optional OptoTerminal-G20 diagnostic display or breakout rack.
ON Voltage
10 VDC @ 0.5 mA
-10 VDC @ 0.5 mA
2.5 VDC @ 0.5 mA
-2.5 VDC @ 0.5 mA
OFF Voltage
3 VDC @ 0.1 mA
-3 VDC @ 0.1 mA
1 VDC @ 0.1 mA
-1 VDC @ 0.1 mA
Polling time from I/O pro­cessor to module1
2–30 ms typical2
2–30 ms typical2
2–30 ms typical2
2–30 ms typical2
Input Turn-On/Off Time
6 ms
6 ms
6 ms
6 ms
Counting Frequency
(DC input)
0–50 Hz @ 50% duty cycle
Operating Temperature
-20 to 70 °C
-20 to 70 °C
-20 to 70 °C
-20 to 70 °C
Storage Temperature
-40 to 85 °C
-40 to 85 °C
-40 to 85 °C
-40 to 85 °C
UL, CE, RoHS, DFARS; UKCA
CE, RoHS, DFARS
CE, RoHS, DFARS
CE, RoHS, DFARS
Lifetime
Lifetime
Lifetime
Lifetime
* Obsolete product.
1 Affects turn-on and turn-off determination
2 Time varies based on the SNAP PAC I/O processor (brain or on-the-rack controller), processor configuration, and Ethernet host communication activity.
Modules, Cables, and Breakout Boards Compatibility Charts
This document shows which SNAP I/O modules, breakout boards, and cables can be used together.
Comparison Chart: SNAP 4-Channel and High-Density Digital Modules
This document compares 4-channel and high-density SNAP digital I/O modules.
SNAP PAC System Product Guide
SNAP High-Density Digital Modules Data Sheet
SNAP I/O high-density digital modules from Opto 22 provide 16 or 32 digital input or output points in one compact SNAP module. These modules are ideal for OEMs and others who have high point-count applications, or for anyone requiring more than 64 digital points on a single SNAP PAC rack. The high-density configuration reduces per-point costs of digital I/O systems by providing up to eight times as many I/O points in the same space.
SNAP high-density digital modules are part of the SNAP PAC System. They can also be used as part of intelligent remote I/O with an Allen-Bradley Logix PLC system. HDD modules require a SNAP PAC R-series controller or a SNAP PAC brain for I/O processing.
This data sheet covers the following modules:
The data sheet also covers the following accessories used with SNAP HDD modules:
SNAP High-Density Digital Module User's Guide
This guide covers how to install and test SNAP 16-channel and 32-channel digital modules, part of the SNAP PAC System. These modules provide 16 or 32 points of digital input or digital output in the same space as a 4-channel digital module. They are ideal for OEMs and for anyone who needs up to 512 digital points on a single mounting rack. SNAP high-density digital modules include the following part numbers:
  • SNAP-IAC-16
  • SNAP-IAC-A-16
  • SNAP-IAC-K-16
  • SNAP-IDC-16
  • SNAP-IDC-32
  • SNAP-IDC-32D
  • SNAP-IDC-32DN
  • SNAP-IDC-32-FM [OBSOLETE]
  • SNAP-IDC-32N
  • SNAP-ODC-32-SNK
  • SNAP-ODC-32-SNK-FM  [OBSOLETE]
  • SNAP-ODC-32-SRC
  • SNAP-ODC-32-SRC-FM  [OBSOLETE]
Video: Securing SNAP Module
Video: Removing a SNAP Module
Accuracy vs Resolution