KB48056
Published: April 21, 2006
Serial B3000 issues in firmware versions 81.30 and 81.31
Problem was discovered in version: 81.30
Released version problem is resolved in 81.32
Various symptoms are apparent when using serial B3000 brains with version 81.30 or 81.31 firmware. They are characterized by the following:
- Averaging does not work on the second channel of analog modules.
- Periodic zero readings possible on any analog module. Readings are typically normal.
- Some analog modules may report a value of ‑32768.
- Scanning issues resulted in I/O readings not being updated.
Brain firmware version 81.32 corrects these issues. Determine the firmware version in your serial B3000 using the suggested methods:
If you are using OptoControl:
- A serial B3000 unit may represent up to two digital I/O units, and two analog I/O units. Select one of the configured I/O units to inspect in Debug mode.
- In Debug mode, double-click the I/O unit in the strategy tree. The View I/O Unit window appears.
- The version is listed under Firmware Version.
- If the version is within the affected version range, contact Opto 22 Product Support.
If you are using a custom application in a Windows environment:
If you are experiencing the above symptoms and are using a custom application in a Windows environment, contact Opto 22 Product Support to determine the firmware revision.