KB48061
Published: April 24, 2006
Revision: 4.0
Engineering unit scaling issue when using serial B3000 with SNAP‑AIVRMS and SNAP-AIARMS modules
Problem was discovered in version: 81.25
Released version problem is resolved in 81.32
Engineering unit scaling does not work properly when using the serial B3000 with SNAP-AIVRMS and SNAP-AIARMS modules.
Brain firmware version 81.32 corrects this issue. Determine the firmware version in your serial B3000 using the suggested methods:
If you are using OptoControl:
- A serial B3000 unit may represent up to two digital I/O units, and two analog I/O units. Select one of the configured analog I/O units to inspect in Debug mode.
- In Debug mode, double-click the I/O unit in the strategy tree. The View I/O Unit window appears.
- The version is listed under Firmware Version.
- If the version is within the affected version range, contact Opto 22 Product Support.
If you are using a custom application in a Windows environment:
If you are experiencing the above symptoms and are using a custom application in a Windows environment, contact Opto 22 Product Support to determine the firmware revision.