KB48091
Published: April 21, 2006
Analog inputs configured as scalable, report a fixed value corresponding to 0 counts on serial B3000
B3000
Analog input modules configured with custom scaling (OptoControl or ioControl), or engineering unit scaling (custom application communicating directly to I/O) in positions 8, 10, 12, and 14, may consistently report a scaled reading corresponding to 0 counts on serial B3000 I/O units.
Example 1: A SNAP-AIV (-10V to 10 V) module is configured for 0 to 10 V and scaled for 0 to 100%. The reading by the B3000 is always 0%.
Example 2: A SNAP-AIMA (-20 mA to 20 mA) module is configured for 4 to 20 mA and scaled for 0 to 100%. The reading by the B3000 is always –25%.
Clearing the serial B3000 EPROM corrects the problem. Modules without scaling do not exhibit the symptoms.
To clear the serial B3000 EPROM, refer to the following directions.
From OptoControl:
1. From OptoControl Debug mode, double-click the B3000 I/O units in the strategy tree.
2. Click the EEPROM Clear button.
If you are using a custom application in a Windows environment:
If you are experiencing the above symptoms and are using a custom application in a Windows environment, contact Opto 22 Product Support.
This problem was discovered September 29, 2005. Brains marked with a date code of 10/05 (October 2005) or newer, do not have this problem.