KB57195
Published: October 12, 2007
Repeated use of 'Set TPO Percent' PAC Control command, keeps output point turned on
SNAP-UP1-ADS
SNAP-UP1-M64
SNAP-UP1-D64
SNAP-LCE
Problem was discovered in version: R7.0a
Problem is fixed in version: R8.1a for SNAP PAC
Changing the TPO percentage on an output point results in the TPO cycle restarting immediately, using the new percentage. This can be a problem if the percentage is written in a programming loop and is updated faster than the cycle period, not allowing the output to ever turn off.
To work around this problem, add a delay to the strategy logic to make sure the programming loop does not loop through faster than the TPO cycle period.
Opto 22 has resolved this issue for SNAP PAC control engines.