KB80117
Published: July 18, 2008
Changing the PID setpoint may cause a jump in the PID output
SNAP-PAC-EB1
SNAP-PAC-EB2
SNAP-PAC-SB1
SNAP-PAC-SB2
Problem was introduced in version: R8.0a for SNAP PAC firmware
R1.0 for Ultimate I/O firmware
Problem is fixed in version: R8.2a for SNAP PAC firmware
See RESOLUTION for information about Ultimate I/O firmware
Changes to a PID setpoint may cause the PID output to jump if the setpoint change is too large relative to the PID scan rate.
Opto 22 has resolved this issue in SNAP PAC firmware.
This issue will not be fixed in Ultimate I/O firmware, as Ultimate I/O is a legacy product.