KB80480
Published: May 12, 2010
Revision: 4.0
Points 4 through 7 on a Snap-AICTD-8 always report °C
Problem was discovered in version: R8.2a
Problem is fixed in version: R8.5c
Points 4 through 7 on a SNAP-AICTD-8 module always report temperatures in degrees Celsius (°C), even if they are configured by a SNAP-PAC controller to report temperatures in degrees Fahrenheit (°F). Points 0 through 3 report temperatures correctly in both Fahrenheit and Celsius degrees.
The incorrect scaling for °F is shown below (Upper Scaled Units = 150, Lower Scaled Units = -273.0). This image shows the problem on point 4.
[image1]
Use PAC Manager to scale points 4 through 7 with the correct Upper and Lower Scaled Units to report temperatures in °F. Then store the values to flash so that they're not overwritten by the strategy when the strategy is started.
The correct °F scaling is shown below for point 0 on a SNAP-AICTD-8 module:
[image1]
Procedure:
  1. Run PAC Manager.
  2. Enter the controller IP address in the Device Name field and click Status Read. Verify you have a valid connection to the controller.
  3. Click Point Config and click on the module number of your SNAP-AICTD-8.
  4. Click in the Value field for the Upper Scaled Units.
  5. Enter 302.0.
  6. Click in the Value field for the Lower Scaled Units.
  7. Enter -459.4.
  8. Click Apply.
  9. Click Status Write. The window shows the Status Write fields and Operation Commands.
  10. Select the Store configuration to flash command and click on Send Command. The new scaled values are stored to flash memory and will not be overwritten by a PAC Control strategy.