KB80531
Published: March 3, 2009
Type R thermocouple readings are about half of the expected values in OptoControl
FACTORYFLOOR - OptoControl
Problem was discovered in version: R4.1a
Type R thermocouple points are incorrectly scaled when a Cyrano strategy is opened and converted in OptoControl. Readings are roughly half of what they should be.
To correct the problem, open the point configuration in OptoControl (double-click the analog point in the strategy tree to get the Edit Analog Point dialog) and click Default in the Scaling section. Compile, and then save the strategy.
Opto 22 is aware of this issue.