KB81008
Published: January 19, 2011
VELOCITY C PID does not calculate Term_P and Term_D
SNAP-PAC-EB1
SNAP-PAC-EB2
SNAP-PAC-EB1-W
SNAP-PAC-EB2-W
SNAP-PAC-SB1
SNAP-PAC-SB2
Problem affects versions: R9.0a and all versions prior to R8.5e
Problem is fixed in version: R8.5e and R9.0b
PID terms Term_D and Term_P are not calculated correctly when the PID input is supplied by the host rather than directly from an I/O point. This problem does not affect PID configurations when the input is supplied directly from an I/O point.
When the PID input is supplied by the host rather than directly from an I/O point, this is always the case: PV = PV_1. This changes the effective equations for Term_P and Term_D as follows:
Velocity Type C:
Term_P = 0
Term_D = 0