KB84022
Published: September 26, 2014
E2 may incorrectly report underrange Optomux counts
Problem affects versions: Firmware R1.1d and lower
Problem is fixed in version: R1.1e
When you are reading Optomux counts from an E2 brain board, you may see counts jump erratically when the input field signal would normally indicate counts of less than -200.
Counts may be far too high (typically in the 10,000-20,000 range, but possibly as high as 61,439). Any value over 10,891 indicates this issue. These erratic values may be interspersed with jumps to -4096.
Correct behavior is that you can measure underrange counts down to -386, with the value jumping between the actual and -4096. Below -386, counts jump back up to 10,891, again alternating with -4096.