KB84812
Published: April 1, 2016
Analog minimum value request in PAC Display or OptoOPCServer returns maximum value
SNAP-PAC-S1-FM
SNAP-PAC-R1-B
SNAP-PAC-R1-FM
SNAP-PAC-R2-FM
SOFTPAC
Problem affects versions: Firmware R9.4b-R9.4c
Problem is fixed in version: Firmware R9.5a
In PAC Display or OptoOPCServer, when you request an analog point's minimum value via the controller, you receive instead the current analog maximum value. Reading the value directly from the I/O unit is not affected.
In PAC Display, read the I/O data directly from the I/O (rather than through the controller). Or modify the strategy to retrieve the analog point's minimum value and store it to a float variable, and have PAC Display read the data from the variable.
OPC client users should read the value directly from the I/O unit by using the MMIO scanner.