KB85078
Published: October 1, 2015
SNAP-AIMV-4 module with point configured as +/- 75 mV shows incorrect default scaling
SNAP-PAC-EB1
SNAP-PAC-EB1-FM
SNAP-PAC-EB1-W
SNAP-PAC-EB2
SNAP-PAC-EB2-FM
SNAP-PAC-EB2-W
SNAP-PAC-SB1
SNAP-PAC-SB2
SNAP-PAC-R1-B
SNAP-PAC-R1-FM
SNAP-PAC-R2-FM
Problem affects versions: Firmware R7.1h through R9.4c
Problem is fixed in version: Firmware R9.5a
This issue occurs only if you are configuring the module without using PAC Manager or PAC Control.
A SNAP PAC brain or rack-mounted controller incorrectly sets the default scaling of a +/- 75 mV point on a SNAP-AIMV-4 module to the following:
Upper Scale: 75 mV
Lower Scale: 75 mV
Values should be:
Upper Scale: 75 mV
Lower Scale: -75 mV
Manually set the upper and lower scaling for this unit to +75 mV and -75 mV respectively.