KB87961
Published: February 27, 2019
Redundant system controller host task may become inaccessible
PAC firmware for:
SNAP-PAC-S1-FM
PAC firmware R9.0a to current, until fixed
PAC firmware R10.0f
Occasionally, when a redundant system switches controllers, one of the controllers may become inaccessible, leaving the system in an error state.
If this issue occurs, both controllers must be restarted:
- Reset controller 1 by writing a "1" to arbiter MMP location 0xf8000200.
- Reset controller 2 by writing a "2" in the same manner.
if that doesn't work, write the same values instead to 0xf8000204 to force a reset.