KB91081
Published: June 11, 2025
Revision: 4.0
TCP connection attempts to port 2001 (OptoMMP) or port 502 (Modbus) may fail
- GRV-EPIC-PR1
- GRV-EPIC-PR2
groov RIOs:
- GRV-R7-MM1001-10
- GRV-R7-MM2001-10
- GRV-R7-I1VAPM-3
For groov EPICs: All versions prior to 4.0.0
For groov RIOs: All versions prior to 4.0.0
4.0.0
When host software attempts to open an OptoMMP (TCP) or Modbus/TCP connection, the connection may be refused, even though connections to other services (like groov Manage or the controller) continue to operate normally.
If you are currently experiencing this issue, restart the processor or module in one of the following ways:
- From the groov Manage Home page, click System > Restart. At the prompt, click Restart.
- Cycle power.
To prevent the issue from occurring again, set a non-zero value to memory map address 0xF0380020. Typically, a value of 60,000 (60 seconds) is sufficient.