KB91120
Published: September 30, 2025
Communication to EPIC I/O unit does not reenable
- GRV-EPIC-PR1
- GRV-EPIC-PR2
Firmware for the following SNAP PACs:
- SNAP-PAC-S2, SNAP-PAC-S2-W
- SNAP-PAC-R1, SNAP-PAC-R1-FM, SNAP-PAC-R1-W, SNAP-PAC-R1-B
- SNAP-PAC-R1 (GEN2)
- SoftPAC
For groov EPICs: 3.0.0 to 3.6.0
For SNAP PACs: R10.4c to R10.5g
For groov EPICs: 4.0.0
For SNAP PACs: R10.6a
If you configured Ethernet redundancy in your PAC Control strategy and the strategy configures a groov EPIC I/O unit with the Eth0 address as primary and the Eth1 address as secondary, the PAC Control Enable Communication to I/O Unit command fails to enable the groov EPIC I/O unit if it is used after this sequence:
- There was a loss of communication with Eth0, which led to a switch from Eth0 to Eth1, then
- there was a loss of communication with Eth1 while Eth0 was unavailable, leading to communication to the I/O unit becoming disabled, then
- Eth1 became available again.