KB50250
Published: July 8, 2008
Problems with the OptoControl AB Integration Kit
Allen-Bradley DF1 Integration Kit for OptoControl
Problem was discovered in version: R3.0
Problem is fixed in version: R4.0
Reading binary files fails when using the AB Typed Read subroutine. There is a missing connection from block 613 to block 614.
Error -60 is added each time subroutines AB Protected Typed Logical Read and AB Protected Typed Logical Write are called (such as from the AB SLC Master example strategy). Pointer table AB_MASTER_POINTER_TABLE is incorrectly initialized in block 262 of the Powerup chart. The ASCII_DATA string table should be moved to AB_MASTER_POINTER_TABLE[2], but instead AB_MASTER_INTEGER_TABLE was moved to that pointer table element.
Opto 22 has resolved these issues.