KB58672
Published: October 12, 2007
Numeric recipe table indices are reset when >2047
Problem was discovered in version: R8.0k
Problem is fixed in version: R8.1a
If an upload recipe results file with an integer or float table has more than 2048 consecutive elements, and the table is divided into more than one section (group of 2048 consecutive elements), then the indices for the sections after the first section restart at 0. The table element values are correct, but the the indices are incorrect.
Example:
An integer table is divided into 2 sections: elements 0 – 2047, and elements 2048 – 3000.
Indices 0 – 2047 are correctly listed in the results file, but indices 2048 – 3000 are listed as 0 – 952.
Sample recipe results file:
My_Control_Engine: Integer Table.My_Integer_Table
0: <value>
1: <value>
2047: <value>
0: <value>/This should read: 2048: <value>
1: <value> /This should read: 2049: <value>
952: <value>/This should read: 2999: <value>