SNAP-AIV-32-FM
SNAP-AIV-32-FM
OBSOLETE SNAP 32-Ch -10VDC to +10VDC Analog Input Module
Please consider SNAP-AIV-32 or contact Opto 22 Pre-Sales engineers for more information.
The SNAP-AIV-32-FM analog input module provides 32 channels of analog voltage input. Each channel can be configured for -10 to +10 VDC or -5 to +5 VDC operation. Although the 32 channels are not isolated from each other, the module is transformer isolated and optically isolated from other modules and devices.
Compatibility: This module can be used only with SNAP PAC brains and on-the-rack controllers.
For field wiring, use the SNAP-HD-CBF6 wiring harness with flying leads, or the convenient SNAP-AIV-HDB-FM breakout board with a SNAP-HD-BF6 cable.
Other options: Build your system in the SNAP I/O Configurator.
Input Range
From -10 volts to +10 volts
From -5 volts to +5 volts
Over-Range Limits
From -11 to +11 volts (+/-10 V range)
From -5.5 to +5.5 volts (+/-5 V range)
Resolution
0.4 mV when configured -10 to +10 volts
0.2 mV when configured -5 to +5 volts
Input Filtering
-3 dB @ 31 Hz
Data Freshness (Max)
1.1 s
DC Common Mode Rejection
>-120 dB
AC Common Mode Rejection
>-120 dB @ 60 Hz
Maximum Survivable Input
220 VAC or 300 VDC
Maximum Operating Common Mode Volt­age
250 V
Accuracy
0.05%, 5 mV @ 10 VDC
2.5 mV @ 5 VDC
Gain Temperature
Coefficient
30 PPM/ °C
Offset Temperature Coefficient
15 PPM/ °C
Isolation
1500 V
Power Requirements
5 VDC (±0.15) @ 150 mA
Input Resistance
1 M ohms (each channel; all channels share the same reference point)
Ambient Temperature:
 Storage
-20 °C to 70 °C
-40 °C to 85 °C
Humidity
5-95%, non-condensing
Torque,
hold-down screws
Torque,
connector screws
5.22 in-lb (0.59 N-m)
CE, RoHS, DFARS; UKCA
Lifetime
Video: Securing SNAP Module
Video: Removing a SNAP Module
Accuracy vs Resolution